ON MOST schemes, the architectural design of. Flexible strategy. Case study. The Forum

Size: px
Start display at page:

Download "ON MOST schemes, the architectural design of. Flexible strategy. Case study. The Forum"

Transcription

1 Flexible strategy ON MOST schemes, the architectural design of a building is influenced by fire engineering strategy. This could be in the form of visual, physical elements such as fire doors, fire curtains, compartment walls and ventilation vents, and also hidden technical provision, such as sprinklers, smoke detection and smoke ventilation. Yet, fire engineering strategies resulting from performance-based design principles do not necessarily need to influence or disturb the architectural design by adding physical elements. Frequently, fire engineering techniques can The Forum Case study be applied which achieve compliance with the Building Regulations, but may not follow current statutory guidance documents, such as Approved Document B of the Building Regulations (ADB) 1. By considering the unique challenges of an individual building, a bespoke fire engineering approach can offer a higher degree of flexibility and the possibility of more than one design solution, to help support the architect s vision and achieve a more cost-efficient design solution. This is illustrated by the following in-depth case study of a building scheme designed for flexible use. Currently under construction, The Forum Southend-on-Sea (as it is known) is a new-build development undertaken for the University of Essex, South Essex College and Southend-on-Sea Borough Council. Due to open in summer 2013, the building comprises five levels (lower ground to third floor) and includes a café, lecture theatre, children s library, creative hub, library, reading area, academic hub, teaching and learning areas, stores and offices. The design team consisted of architects, civil and structural engineers, acoustic and lighting engineers, and fire engineers. The scheme has demonstrated that, for a fire engineered strategy to be successful, fire engineers must be part 38 April

2 Karl Wallasch shows how fire engineering solutions can ensure fire protection while supporting the unique aspirations of buildings to benefit architects, clients and end-users of the design team at an early stage in order to highlight potential life safety risk and areas where descriptive codes may unnecessarily detract from the architectural vision and, where instead, a fire engineering strategy may allow the unique aspirations for the building to be achieved. Initial advice The initial architectural concept allowed for four stair cores. From experience, the fire engineers, Hoare Lea Fire Engineering (HLFE), felt that the number of stairs and stair widths could be reduced, when taking into account the technical provisions planned for the building such as automatic fire detection and voice alarm. They demonstrated to the architect and clients that the Figure 1: 3D section showing internal open stair serving ground to third floor levels, and lecture theatre connecting lower ground and ground floor (ADP Architects) building could be designed in accordance with ADB, with reference to British Standard (BS) Based on initial means of escape calculations, the architect was advised that three stairs were sufficient, with at least two of them serving all levels and located at each end of the building. As the height of the building is greater than 7.5m, but less than 18m, firefighting shafts (which did not need to include firefighting lifts) were required. Due to the shape of the building, these were also located at either end. Client requirements The scheme is designed to accommodate three clients with different aspirations and needs, which presented some challenges regarding integration and management. Southend-on-Sea Borough Council intends to use the lower floor as a library and for presenting plays, films, live music and indoor sporting events, and there is a requirement also to serve hot food and drinks. The University of Essex wishes to use the building as an assembly recreational building for activities such as public lectures, conferences and exhibitions, and as an office space. South Essex College aims to use the building for similar educational and office purposes, including teaching rooms, open space and enclosed learning and meeting spaces. It is likely therefore, that The Forum Southend-on-Sea will be used by members of the public who are unfamiliar with the building. One aspect of the fire engineering strategy was to address the clients management strategies applicable when the entire building is occupied, as well as the strategies to be applied during times when only parts of the building such as the teaching rooms, gallery space, lecture theatre or cafe are in use. The architectural concept reflects this need for flexibility of use and the building is designed so that it can be divided into open and closed sections, or used as one large circulation space by different user groups. Design concepts Generally, architectural concepts consider circulation and movement of occupants within a building during normal use. Following the introduction of the Building Regulations, any building should be designed with the provision to allow for an early warning of fire and appropriate means of escape in case of fire, from the building to a place of safety. A fire engineering concept can allow for a safe means of escape by looking at the interaction between structural elements, such as protected escape corridors; technical fire precautions, for example automatic fire and smoke detection and ventilation; and management within a building. Forum fire precautions As a central atrium links all floor levels, it was stated at an early stage that, due to adjacent buildings, some degree of compartmentation was likely to be required to restrict external fire spread. April

3 Following a detailed external fire spread analysis based on the British Research Establishment s publication, External fire spread: building separation and boundary distances 3, it was suggested to the architects that it would be acceptable to link the ground and first floor, but that the second and third floor levels should be separated from the atrium via firerated glazing. Neither Approved Document B nor BS 9999 classifies the void as an atrium and therefore a dedicated smoke clearance system was not required. In addition, the means of escape strategy required a minimum distance of 4.5m from the edge of the void. Two means of escape stairs were proposed at either end of the building, and therefore at least one means of escape route was away from the void. A summer peak-time ventilation system in the atrium, linked to a firefighter s switch, allows the fire and rescue service to use the system to clear smoke. This assists the speed with which the building can return to normal operation and gives a higher degree of property protection. Lecture theatre The internal lecture theatre on the ground and lower-ground floors can accommodate 203 people. Means of escape is provided via two exits into the ground floor level area. An evacuation lift also serves the lower ground floor level up to ground floor level. At an initial meeting with building control officers and the clients fire officers, it was highlighted that occupants from the lecture theatre should be able to escape into a place of relative safety (the reception space at ground floor) and from there to a place of safety outside. A major concern was the means of escape of non-ambulant persons from the lower ground floor level of the lecture theatre. The following options were discussed: Option 1: Provision of at least one safe route from the lower-ground Figure 2: 3D geometry of The ForumSouthend-on-Sea used for the RSET analysis (HLFE) floor level of the lecture theatre to outside (via either protected corridor or protected stair). Option 2: Provision of an evacuation lift, serving the lower-ground to ground-floor level, and a higher degree of compartmentation in the main reception area at ground-floor level to create a protected route from the lecture theatre directly to the outside (eg provision of fire and smoke curtains). Option 3: The use of a fire engineered design solution, consisting of a comparison between the Required Safe Egress Time (RSET) and the Available Safe Egress Time (ASET). RSET is the time required by lecture theatre occupants to leave the building and escape to a place of safety, such as outside. ASET is the time available for occupants to escape before conditions within a building become untenable for escape due to fire and smoke spread. Typically, a successful fire engineered solution would demonstrate that RSET is less than ASET (RSET < ASET). Advanced (or evacuation) modelling was used to predict the time for an evacuation of the building (RSET); and a computational fluid dynamics (CFD) analysis was used to predict the time when conditions would become untenable (ASET). Evacuation model - RSET The RSET analysis consists of fire engineering calculations to determine the detection time, the time to activate alarm, premovement time and travel time required for escape. This is conducted in accordance with the British Standard document, PD : and CIBSE Guide E: Fire safety engineering, The RSET study for this development included all floors, interior walls, doors and stairs. The calculations for detection time, alarm time and pre-movement time were based on the following: clear ceiling height at ground floor level: 4m maximum distance between centre of fire and detector: 5m simultaneous evacuation for the entire building alarm time is based on automatic fire detection raised by a single-knock pre-movement time will vary between 30 seconds (for first few occupants) and 90 seconds (for last few occupants) all assumptions follow guidance of PD Evacuation scenario Different evacuation scenarios were developed, with different exits from the lecture theatre available, depending on the proposed fire location. Based on discussions with the clients and the building control officer, it was decided that one exit (exit 012) of the lecture theatre should not be used. Occupants therefore needed to escape via exit 013 into the open space at ground floor (see Figure 3). In the case of the proposed worst fire location, the main front exits 001 and 014 could be blocked, therefore these are not used within the evacuation model. All other exits and escape routes are available. The total occupant load has been assumed to be 2,235, including 203 occupants in the lecture theatre. 40 April

4 Figure 3: Ground floor layout (as STEPS model) outlining evacuation scenario 1 (HLFE) Computer software The computer evacuation model used to demonstrate people movement within the lecture theatre was Simulation of Transient Evacuation and Pedestrian movements (STEPS), designed to predict pedestrian movement under normal and emergency conditions. Producing real-time 3D simulations in an easily understandable graphic form allows the results to be interpreted by both non-specialists and experts. This helps to identify natural bottlenecks and preferred exits, as well as testing evacuation routes and timings for different emergency scenarios. CFD modelling was used to determine the ASET, when occupants exposed to a fire are likely to be unable to evacuate due to the effects of exposure to smoke, radiant heat and toxic gases. Using the National Institute of Standards and Technology s (NIST s) computer modelling software Fire Dynamics Simulator (FDS) 6,7, the time to untenable conditions was calculated and presented in visual formats. Some basic assumptions were made for modelling purposes. Geometry HLFE included ground and first floors as well as the void above only. The CFD model did not include the second or third floor, as these will be separated by fire-rated construction (see Figure 4). Electrical Product Safety Conference 2013 Safety of electrical products - a approach 16 May 2013 Church House Westminster London Only 75 An Electrical Safety Council event bringing together professionals with an interest in electrical product safety and consumer protection. Keynote speech from Malcolm Harbour CBE, MEP For further information and to book: The agenda will cover: Communication of risk Product recall processes Traceability Safety in design April

5 Fire size The area within the open space in front of the lecture theatre is mainly used as circulation space. However, close to exit 001 there is a buggy store, and tables and chairs from the café store are located on both sides of the lecture theatre. Furthermore, the main reception area is also located at ground floor level. Following guidance of the CIBSE Guide E, a heat release rate of 290 kw/m 2 was used and a total fire area of 4.0m 2 (2m by 2m). Based on the use of the building a medium fire growth rate was implemented. Fire scenarios The three fire scenarios differ in terms of fire location. Scenarios 1 and 2 assume that one exit of the lecture theatre is blocked due to a fire. This assumes the worst case of evacuation time required to empty the entire lecture theatre. In scenario 1, the fire location also blocks the main exit the widest exit of the building - delaying the total evacuation time. In the third scenario the fire location was chosen to be located near the evacuation lift, which links lower ground and ground floor. RSET-ASET results The CFD software, FDS and Smokeview by the US National Institute of Standard and Technology (NIST) were used. The design criteria assessing tenability Figure 4: Proposed 3D Geometry via FDS/ Smokeview (HLFE) considered minimum visibility, maximum temperature and toxic gases, as outlined in PD : 2004 and the CIBSE Guide E, Results of the CFD modelling indicated that a maximum evacuation time of 4 minutes and 5 seconds is required (this includes evacuation of wheelchair users) and that conditions become untenable after 6 minutes. The results of the modelling also indicated that the provision of smoke curtains would stop smoke spread into the means of escape routes mainly used by non-ambulant persons. It was therefore suggested to the design team that the installation of smoke curtains would increase the level of safety, maintaining a safe route clear of smoke for more than 360 seconds, thereby demonstrating a safe means of escape for occupants from the entire building, including the lecture theatre. The results of the RSET-ASET study were presented to the design team, the clients fire officers and the statutory authorities (building control and fire Officer) in the form of a presentation of the CFD video files. A comprehensive CFD report that accompanied the main fire strategy report also included the full analysis. The statutory authorities agreed that the level of safety had been significantly enhanced by the provision of the smoke curtains. The fire engineered strategy resulted in design implications and benefits. The modelling techniques employed required intense discussions with all parties and the simulation techniques resulted in a time-intensive approval process. Clear benefits were achieved. The strategy fits the use and architectural design of the building, allowing for a higher degree of flexibility, a reduced number of stair cores and the outlining of options for means of escape strategy from the lecture theatre, while negating the need for smoke ventilation. In addition, the performance-based design has allowed for a reduction in the number of escape stairs within The Forum Southend-on- Sea, freeing up space and assisting in achieving a cost-efficient design Karl Wallasch is executive engineer at Hoare Lea Fire Engineering References 1. Approved Document B (Fire Safety) Volume 2: Buildings other than dwelling houses, BS 9999: Code of practice for fire safety in the design, management and use of buildings, October BR 187: External fire spread: Building separation and boundary distances, BRE, PD : The application of fire safety engineering principles to fire safety design of buildings: Part 6: Human factors. Life safety strategies. Occupant evacuation, behaviour and condition (Sub-system 6), BSI, CIBSE Guide E: Fire safety engineering, 3rd Edition, The Chartered Institution of Building Services Engineers, London, May Fire Dynamics Simulator (Version 5) User s Guide, NIST Special Publication , FDS Version 5.5, October Fire Dynamics Simulator (Version 5) Technical Reference Guide, NIST Special Publication , Volume 1: Mathematical Model, FDS Version 5.5, October April

Wyoming State Capitol Building Restoration and Modernization

Wyoming State Capitol Building Restoration and Modernization Wyoming State Capitol Building Restoration and Modernization Level I / II Life Safety and Fire Protection Assessment 25 September 2013 Presentation Overview Project Overview Applicable Codes Non-Conformance

More information

Area of Rescue Assistance Communication System ADA Code Applicable excerpts:

Area of Rescue Assistance Communication System ADA Code Applicable excerpts: Area of Rescue Assistance Communication System ADA Code Applicable excerpts: CONTENTS (Guidelines and Definitions) Page 1 Area of Rescue Assistance Requirements Page 2 Emergency Communication Equipment

More information

Fire Safety Risk Assessment

Fire Safety Risk Assessment 1 Sources of ignition The main sources of ignition in Cass building are: PAF arrange for the fixed electrical installation to be tested in accordance with the British Standards. Test certificates are kept

More information

Improving fire safety through engineering (rational designs)

Improving fire safety through engineering (rational designs) Improving fire safety through engineering (rational designs) Johan van den Heever Fire Safety Indaba, Cape Town 2013 'Promoting responsible fire safety in Southern Africa' 1 Introduction What is fire safety

More information

Grasshoppers Rugby Football Sports and Social Club. The Fire Risk Assessment

Grasshoppers Rugby Football Sports and Social Club. The Fire Risk Assessment Grasshoppers Rugby Football Sports and Social Club The Fire Risk Assessment Revision 1 Dated: 15th February 2013 CONTENTS 1. PREMISES DETAILS 2. PREMISES PLAN 3. HAZARDS 4. HISTORY 5. MITIGATING THE EFFECTS

More information

Building evacuation, rules and reality

Building evacuation, rules and reality Building evacuation, rules and reality Peter van de Leur DGMR Raadgevende Ingenieurs BV, Den Haag, the Netherlands The paper discusses some of the problems surrounding the simulation of the evacuation

More information

FIRE SAFETY RISK ASSESSMENT

FIRE SAFETY RISK ASSESSMENT FIRE SAFETY RISK ASSESSMENT For small single occupancy premises Premises Hertco Ltd ACME House, Old London Road, Hertford SG17 7LD Fire Safety Risk Assessment for Small Premises Introduction Regulatory

More information

Guidance on loft conversions in two-storey houses

Guidance on loft conversions in two-storey houses Guidance on loft conversions in two-storey houses Technical guidance for building control surveyors, designers and installers 01 Guidance on loft conversions in two-storey houses Technical guidance for

More information

A study of the nature of fire risks in tall buildings

A study of the nature of fire risks in tall buildings A study of the nature of fire risks in tall buildings David Charters and Carl Sherwood BRE Global 12 th March 2013 Part of the BRE Trust Overview 1. Introduction 2. Challenges of tall buildings 3. Analysis

More information

Introduction. CE marked construction products

Introduction. CE marked construction products Introduction This Technical Booklet has been prepared by the Department of Finance and Personnel and provides for certain methods and standards of building which, if followed, will satisfy the requirements

More information

- 5 - Table1. Maximum Compartment Volumes

- 5 - Table1. Maximum Compartment Volumes - 5 - Part II - SPECIFIC REQUIREMENTS 5. Compartmentation 5.1 Every building should be divided into compartments by walls and floors to inhibit the spread of fire. 5.2 Compartment walls, compartment floors,

More information

Fire Safety Risk Assessment Checklist for Residential Care Premises

Fire Safety Risk Assessment Checklist for Residential Care Premises Checklist for Residential Care Premises Name of Premises: Address of Premises: Name of Responsible Person: What area / location does the assessment cover? Does the assessment cover the whole site YES or

More information

Overview of Hotel Fire Safety Requirements

Overview of Hotel Fire Safety Requirements Overview of Hotel Fire Safety Requirements in the Fire Code Susan Clarke, P.Eng. Office of the Fire Marshal - January 10, 2012 1 Agenda Regulation History - Hotels Fire Code Overview (Parts 1 to 8) Defined

More information

Fire. The Fire Installers Mate. A guide to fire alarm systems design

Fire. The Fire Installers Mate. A guide to fire alarm systems design Fire The Fire Installers Mate A guide to fire alarm systems design BS 5839 Part 1:2002 A guide to BS 5839 Part 1:2002 Disclaimer This booklet is not intended to be a comprehensive guide to all aspects

More information

GENERAL FIRE SAFETY TERMS & DEFINITIONS

GENERAL FIRE SAFETY TERMS & DEFINITIONS UCL Fire Technical Note - TN006 Fire Safety Technical Guide GENERAL FIRE SAFETY TERMS & DEFINITIONS Reference: BS4422-2005 Fire Safety Vocabulary - for further information and definitions BS EN ISO 13943-2000:

More information

UPP Residential Services Fire Risk Assessment

UPP Residential Services Fire Risk Assessment UPP Residential Services Fire Risk Assessment TS11151-R02-DRAFT1 15 August 2011 for: Keynes College University Road Canterbury Kent Recommended latest review date 14 August 2011 Executive summary This

More information

FIRE RISK ASSESSMENT WORKED EXAMPLE

FIRE RISK ASSESSMENT WORKED EXAMPLE FIRE RISK ASSESSMENT WORKED EXAMPLE 1 PREMISES PARTICULARS BE-INT05 Premises Name S M Enterprises Address Small Place Medium Road Anywhere Tel no: 01234 567890 Date of Risk Assessment 1 st July 2011 Use

More information

If you require any assistance with smoke control systems we can be contacted as follows:

If you require any assistance with smoke control systems we can be contacted as follows: This document provides guidance relating to the design, installation and commissioning of smoke ventilation systems within the common escape routes in apartment buildings. Although the prevention of smoke

More information

Proposed changes to the Acceptable Solution for Building Code clause F7 (Warning Systems) Proposed amended Acceptable Solution for Warning Systems

Proposed changes to the Acceptable Solution for Building Code clause F7 (Warning Systems) Proposed amended Acceptable Solution for Warning Systems Proposed changes to the Acceptable Solution for Building Code clause F7 (Warning Systems) Appendix A Proposed amended Acceptable Solution for Warning Systems s in the grey boxes form part of the proposed

More information

Building Control Guidance Note

Building Control Guidance Note Issued 01/01/13 Rev Page 1 of 5 If you intend to convert an existing loft space into additional rooms you will need to apply for Building Regulation Approval. You may also need Planning Permission if you

More information

REVIEW ON FIRE REGULATIONS FOR NEW HIGH-RISE COMMERCIAL BUILDINGS IN HONG KONG AND A BRIEF COMPARISON WITH THOSE IN OVERSEAS

REVIEW ON FIRE REGULATIONS FOR NEW HIGH-RISE COMMERCIAL BUILDINGS IN HONG KONG AND A BRIEF COMPARISON WITH THOSE IN OVERSEAS , Volume 3, Number 1, p.25-51, 2001 REVIEW ON FIRE REGULATIONS FOR NEW HIGH-RISE COMMERCIAL BUILDINGS IN HONG KONG AND A BRIEF COMPARISON WITH THOSE IN OVERSEAS W.Y. Hung and W.K. Chow Department of Building

More information

SPECIFIC GUIDANCE FOR A HOUSE IN MULTIPLE OCCUPATION (HMO) CONVERTED ENTIRELY INTO SELF CONTAINED FLATS

SPECIFIC GUIDANCE FOR A HOUSE IN MULTIPLE OCCUPATION (HMO) CONVERTED ENTIRELY INTO SELF CONTAINED FLATS Document F SPECIFIC GUIDANCE FOR A HOUSE IN MULTIPLE OCCUPATION (HMO) CONVERTED ENTIRELY INTO SELF CONTAINED FLATS This document is intended as a specific guide for persons who own, manage or control Houses

More information

Piotr Tofiło a,*, Marek Konecki b, Jerzy Gałaj c, Waldemar Jaskółowski d, Norbert Tuśnio e, Marcin Cisek f

Piotr Tofiło a,*, Marek Konecki b, Jerzy Gałaj c, Waldemar Jaskółowski d, Norbert Tuśnio e, Marcin Cisek f Available online at www.sciencedirect.com Procedia Engineering 57 (2013 ) 1156 1165 11th International Conference on Modern Building Materials, Structures and Techniques, MBMST 2013 Expert System for Building

More information

Pearl River Tower, Guangzhou: Fire Protection Strategies for an Energy Efficient High-Rise Building

Pearl River Tower, Guangzhou: Fire Protection Strategies for an Energy Efficient High-Rise Building Pearl River Tower, Guangzhou: Fire Protection Strategies for an Energy Efficient High-Rise Building Fang Li 1, James Antell, AIA, P.E. 2 and Martin Reiss, P.E., FSFPE 3 1 Vice President, China Operations,

More information

Appraisal of Passive and Active Fire Protection Systems in Student s Accommodation

Appraisal of Passive and Active Fire Protection Systems in Student s Accommodation MATEC Web of Conferences 10, 06002 (2014) DOI: 10.1051/ matecconf/ 20141006002 C Owned by the authors, published by EDP Sciences, 2014 Appraisal of Passive and Active Fire Protection Systems in Student

More information

Using Sprinkler Systems in Buildings and Structures Compliance with current fire safety guidance

Using Sprinkler Systems in Buildings and Structures Compliance with current fire safety guidance Technical Guidance Note No 2 Issue No 1: October 2011 ISBN 0-9552628-8-7 Using Sprinkler Systems in Buildings and Structures Compliance with current fire safety guidance In this Technical Guidance Note

More information

AVAILABLE TO DOWNLOAD ON THE APOLLO APP. Fire Alarm Systems Design. a guide to BS5839

AVAILABLE TO DOWNLOAD ON THE APOLLO APP. Fire Alarm Systems Design. a guide to BS5839 AVAILABLE TO DOWNLOAD ON THE APOLLO APP a guide to Fire Alarm Systems Design BS5839 Part1:2013 The Regulatory Reform (Fire Safety) Order (FSO) became law on 1 October 2006 Legally you must comply! What

More information

Services Enclosures and Protected Shafts - Maintaining Compartmentation

Services Enclosures and Protected Shafts - Maintaining Compartmentation Introduction When a fire resisting element is used to provide fire compartmentation, every opening that allows services to pass through the element must be adequately protected by sealing, or fire stopping

More information

Indiana Building Rehabilitation Standard

Indiana Building Rehabilitation Standard Rule 8. Indiana Building Rehabilitation Standard 675 IAC 12-8-1 Definitions Sec. 1. The following definitions apply throughout this rule: (1) "Building code" means the Indiana Building Code under 675 IAC

More information

Fire Alarm system Installation Guide

Fire Alarm system Installation Guide Fire Alarm system Installation Guide Fire Alarm System Categories Systems designed for Protection of Property only, fall into two classifications P1 or P2. but a manual system is also needed, then this

More information

New Ontario Building Code Requirements for Mid-rise Wood Frame Buildings

New Ontario Building Code Requirements for Mid-rise Wood Frame Buildings New Ontario Building Code Requirements for Mid-rise Wood Frame Buildings Note: This information addresses complex issues in a summary fashion. Consideration should be given to the official version of the

More information

Decree of the Ministry of the Environment. on fire safety of garages

Decree of the Ministry of the Environment. on fire safety of garages E4 THE NATIONAL BUILDING CODE OF FINLAND Fire safety of garages Guidelines 2005 Decree of the Ministry of the Environment on fire safety of garages Adopted in Helsinki, 22 March 2005 Pursuant to the Decision

More information

OCFRD TENT STANDARD 6000. This Standard operates under the authority of Orange County, Florida Ordinance and State Statutes.

OCFRD TENT STANDARD 6000. This Standard operates under the authority of Orange County, Florida Ordinance and State Statutes. 1. Authority Orange County Fire Rescue Department Tents & Membrane Structures Office of The Fire Marshall - 109 E. Church Street, Lower Level - Orlando, Florida 32801-3319 Phone: 407-836-0004 Fax: 407-836-8310

More information

IFE Level 4 Certificate in Fire Science and Fire Safety (HL)

IFE Level 4 Certificate in Fire Science and Fire Safety (HL) IFE Level 4 Certificate in Fire Science and Fire Safety (HL) Unit 2: Fire Safety Unit Reference Number: D/505/5932 Introduction This unit focuses on the prevention and detection of fire in premises and

More information

Fire safety advice for landlords

Fire safety advice for landlords YOU CAN PREVENT IT Fire safety advice for landlords Introduction Each year there are over 50,000 fires in dwellings in the UK. These result in around 300 hundred fatalities and several thousand serious

More information

Additional Guidance. for application to. HM Government Guide to Fire Safety Risk Assessment Residential Care Premises

Additional Guidance. for application to. HM Government Guide to Fire Safety Risk Assessment Residential Care Premises Additional Guidance for application to HM Government Guide to Fire Safety Risk Assessment Residential Care Premises Good Practice Guidance 2016 Additional Guidance agreed between the National Association

More information

Fire Risk in Metro Tunnels and Stations

Fire Risk in Metro Tunnels and Stations Fire Risk in Metro Tunnels and Stations Hyder Consulting Presented by: Dr. Leong Poon Ir. Richard Lau 2 Dec 2005 Metro Tunnels and Stations General Characteristics Limited to metropolitan area (hence the

More information

Fire Risk Assessment For Simple Premises

Fire Risk Assessment For Simple Premises Fire Risk Assessment For Simple Premises Responsible Person (Employer or other person having control of the relevant premises) Company / Premises Name Address of Premises Postcode Primary Use of Premises

More information

EVACUATION OF DISABLED PEOPLE (Document under constant review)

EVACUATION OF DISABLED PEOPLE (Document under constant review) EVACUATION OF DISABLED PEOPLE (Document under constant review) HEALTH & SAFETY UNIT JANUARY 2008 CONTENTS PAGE 1. INTRODUCTION... 1 2. PLANNING AN EVACUATION PROCEDURE... 1 3. PERSONAL EMERGENCY EVACUATION

More information

GENERAL + MEANS OF ESCAPE (Part One) By Mdm Eng Yew Hoon (SIA)

GENERAL + MEANS OF ESCAPE (Part One) By Mdm Eng Yew Hoon (SIA) GENERAL + MEANS OF ESCAPE (Part One) By Mdm Eng Yew Hoon (SIA) Chapter 1 : Definitions clause 1.2.10 : circulation space OLD CLAUSE A space mainly used as means of access between a room or protected shaft

More information

FIRE DETECTION AND ALARM SYSTEMS

FIRE DETECTION AND ALARM SYSTEMS HMO Information Sheet No 1 FIRE DETECTION AND ALARM SYSTEMS 1. Introduction When a property is in multiple occupation, the risk of fire breaking out is greater than in an ordinary single family home. Some

More information

UCL FIRE RISK ASSESSMENT POLICY& ARRANGEMENTS

UCL FIRE RISK ASSESSMENT POLICY& ARRANGEMENTS Fire Safety Technical Guide UCL FIRE RISK ASSESSMENT POLICY& ARRANGEMENTS 1.0. BACKGROUND 1.1. The Regulatory Reform (Fire Safety) Order (known Fire Safety Order) applies to England and Wales (Northern

More information

Certification: Building Plans Examiner. Exam ID: B3

Certification: Building Plans Examiner. Exam ID: B3 Certification: Building Plans Examiner Exam ID: B3 Scope: A Building Plans Examiner will be responsible for reviewing submitted plans to determine if they meet the requirements of the various Building

More information

3.In making the following determination, the Secretary of State has not considered whether the plans conform to any other relevant requirements.

3.In making the following determination, the Secretary of State has not considered whether the plans conform to any other relevant requirements. Date: 06/09/99 Ref: 45/1/166 Note: The following letter was issued by our former department, the Department for Environment, Transport and the Regions (DETR). DETR is now Communities and Local Government

More information

BUILDING CONTROL GUIDANCE SHEET SMOKE ALARMS IN STANDARD DWELLINGS Last updated 16/12/2010

BUILDING CONTROL GUIDANCE SHEET SMOKE ALARMS IN STANDARD DWELLINGS Last updated 16/12/2010 Building Control Charnwood Borough Council Southfield Road Loughborough LE11 2TN BUILDING CONTROL GUIDANCE SHEET SMOKE ALARMS IN STANDARD DWELLINGS Last updated 16/12/2010 Page 1 of 7 PURPOSE: This Guidance

More information

James R. Quiter, P.E., Senior Vice President Rolf Jensen & Associates, Inc.

James R. Quiter, P.E., Senior Vice President Rolf Jensen & Associates, Inc. AT THE STRATOSPHERE TOWER, LAS VEGAS NEVADA By: James R. Quiter, P.E., Senior Vice President Rolf Jensen & Associates, Inc. INTRODUCTION This paper discusses the performance based approach to fire protection

More information

Northern Ireland Housing Executive: HMO Fire Safety Guide

Northern Ireland Housing Executive: HMO Fire Safety Guide Northern Ireland Housing Executive: HMO Fire Safety Guide Contents Equality Statement 5 Houses in Multiple Occupation (HMOs) means of escape in case of fire and other fire precautions 6 1.0 Introduction

More information

Hotel Fire Safety for staff

Hotel Fire Safety for staff Teaching Guide Hotel Fire Safety for staff Seattle Fire Department Fire Prevention Division Hotel Fire Safety Instructor Outline Introduction Goals: To ensure that hotel employees are knowledgeable in

More information

Fire Safety in High Rise Residential Blocks

Fire Safety in High Rise Residential Blocks Fire Safety in High Rise Residential Blocks What can we learn from Lakanal House? www.labc.co.uk This information paper has been prepared to focus on the lessons learned from the Lakanal House enquiry.

More information

5-8.1.4* Any required illumination shall be arranged so that the failure of any single lighting unit shall not leave any area in darkness.

5-8.1.4* Any required illumination shall be arranged so that the failure of any single lighting unit shall not leave any area in darkness. NFPA 101 Life Safety Code Section 5-8 Illumination of Means of Egress 5-8.1 General. 5-8.1* Illumination of means of egress shall be provided in accordance with this section for every building and structure

More information

Exova Warringtonfire fire safety engineering

Exova Warringtonfire fire safety engineering Consultancy - Fire Engineering Exova Warringtonfire fire safety engineering We are committed to the philosophy where the fire safety design supports the vision, innovation or imagination of the building

More information

CBD-233. Fire Alarm and Detection Systems

CBD-233. Fire Alarm and Detection Systems Page 1 of 5 CBD-233. Fire Alarm and Detection Systems Originally published August 1984. R.H.L. McEwen Fire alarm systems are normally required by building codes. In the case of new buildings, this is usually

More information

LONDON BOROUGH OF BROMLEY STANDARDS FOR HOUSES IN MULTIPLE OCCUPATION (HMO) INTRODUCTION

LONDON BOROUGH OF BROMLEY STANDARDS FOR HOUSES IN MULTIPLE OCCUPATION (HMO) INTRODUCTION LONDON BOROUGH OF BROMLEY STANDARDS FOR HOUSES IN MULTIPLE OCCUPATION (HMO) INTRODUCTION 1. Minimum Standards: This document sets out the minimum standards required in HMOs located within the London Borough

More information

Building Code Clarifications - 7. Fire Resistance

Building Code Clarifications - 7. Fire Resistance Building Code Clarifications - 7. Fire Resistance 7.1 (15-12-030) Use of combustibles in Type III construction roof assemblies Code Section (15-12-030) Use of Combustibles was revised on May 17, 2000,

More information

Educational. Educational-Existing 1/28/2014. OCCUPANT LOADS [no change] Application. Application

Educational. Educational-Existing 1/28/2014. OCCUPANT LOADS [no change] Application. Application February 2014 Code Requirements and Inspections in Educational Occupancies Presented By: Barry W. Rickert Douglas M. Schanne Fire Marshal Training Program Supervisor Office of Education & Data Management

More information

Proposed Residential Complex At Holding No. - 98, B.T. Road, Kolkata - 700090 Developer Premier Mica Mining And Manufacturing Company

Proposed Residential Complex At Holding No. - 98, B.T. Road, Kolkata - 700090 Developer Premier Mica Mining And Manufacturing Company RISK MANAGEMENT PLAN is an integral part of a modernized and sophisticated residential complex. No efforts will be spared in identifying the all possible risks and disasters, evaluating them, installing

More information

Planning Technical Advice Note: Waste bin storage and access requirements for new and change of use developments

Planning Technical Advice Note: Waste bin storage and access requirements for new and change of use developments City Development Planning Technical Advice Note: Waste bin storage and access requirements for new and change of use developments November 2014 1. Introduction There are a number of issues associated with

More information

Contents. 1. Introduction 1.1 Reason for this Guide 3 1.2 Interpretation 1.3 Principles of Fire Safety 1.4 Legal Provisions 4

Contents. 1. Introduction 1.1 Reason for this Guide 3 1.2 Interpretation 1.3 Principles of Fire Safety 1.4 Legal Provisions 4 Contents 1. Introduction 1.1 Reason for this Guide 3 1.2 Interpretation 1.3 Principles of Fire Safety 1.4 Legal Provisions 4 2. Scope and Application 2.1 Scope of the Guide 5 2.2 Premises to which the

More information

SCHOOL FIRE AND LIFE SAFETY INSPECTION CHECKLIST

SCHOOL FIRE AND LIFE SAFETY INSPECTION CHECKLIST SCHOOL FIRE AND LIFE SAFETY INSPECTION CHECKLIST School Name: School Address: Town: Phone: Inspected By (Please Print): Inspection Organization Name: Inspector Phone: Date of Inspection: Building Name:

More information

Pollution CO CO 2. Carbonaceo us soot H 2 S, NOX, SO2

Pollution CO CO 2. Carbonaceo us soot H 2 S, NOX, SO2 Pollution CO CO 2 Carbonaceo us soot H 2 S, NOX, SO2 The National Building Code (NBC) contains set of minimum provisions, designed to protect the safety of the public with regard to structural sufficiency,

More information

Guidance Document on SELECTION AND SPECIFICATION OF FIRE ALARM CATEGORY IN ACCORDANCE WITH BS 5839-1

Guidance Document on SELECTION AND SPECIFICATION OF FIRE ALARM CATEGORY IN ACCORDANCE WITH BS 5839-1 Guidance Document on SELECTION AND SPECIFICATION OF FIRE ALARM CATEGORY IN ACCORDANCE WITH BS 5839-1 FIA Guidance for the Fire Protection Industry This Guidance Note is intended as a general guidance and

More information

I.S. 3218 :2013 Fire Detection & Alarm Systems

I.S. 3218 :2013 Fire Detection & Alarm Systems I.S. 3218 :2013 Fire Detection & Alarm Systems Overview of significant changes 26 th March 2014 FPS Ltd Today s Programme Commencement Transition Competence & Qualifications System Certification System

More information

CITY OF LONDON SCHOOL FOR GIRLS FIRE SAFETY, PROCEDURE AND RISK ASSESSMENT POLICY

CITY OF LONDON SCHOOL FOR GIRLS FIRE SAFETY, PROCEDURE AND RISK ASSESSMENT POLICY CITY OF LONDON SCHOOL FOR GIRLS FIRE SAFETY, PROCEDURE AND RISK ASSESSMENT POLICY This policy was written in July 2014 and will be agreed by the Board of Governors in October 2014. To be reviewed by June

More information

Droveway ARCHITECTURAL SERVICES. Disability Access Audit. Sample Gospel Hall. 22 September 2005. For

Droveway ARCHITECTURAL SERVICES. Disability Access Audit. Sample Gospel Hall. 22 September 2005. For 22 September 2005 Disability Access Audit For Droveway ARCHITECTURAL SERVICES Droveway House 11 Lilac Avenue, Streetly Sutton Coldfield West Midlands B74 3TH Tel : 0121 352 0150 www.droveway.co.uk Page

More information

Health Chapter 420-5-22 ALABAMA STATE BOARD OF HEALTH ALABAMA DEPARTMENT OF PUBLIC HEALTH ADMINISTRATIVE CODE

Health Chapter 420-5-22 ALABAMA STATE BOARD OF HEALTH ALABAMA DEPARTMENT OF PUBLIC HEALTH ADMINISTRATIVE CODE Health Chapter 420-5-22 ALABAMA STATE BOARD OF HEALTH ALABAMA DEPARTMENT OF PUBLIC HEALTH ADMINISTRATIVE CODE CHAPTER 420-5-22 SUBMISSION OF PLANS AND SPECIFICATIONS FOR HEALTH CARE FACILITIES TABLE OF

More information

Fire Alarm Systems Requirements by Occupancy Type

Fire Alarm Systems Requirements by Occupancy Type WALT WHITE Fire Chief 5770 Freeport Blvd., Suite 200 Sacramento, CA 95822-3516 Ph: (916) 808-1300 Fax: (916) 808-1629 www.sacfire.org Fire Alarm Systems Requirements by Occupancy Type 2013 California Building

More information

Compliance Document for New Zealand Building Code Clause F7 Warning Systems Fourth Edition

Compliance Document for New Zealand Building Code Clause F7 Warning Systems Fourth Edition Compliance Document for New Zealand Building Code Clause F7 Warning Systems Fourth Edition Prepared by the Department of Building and Housing This Compliance Document is prepared by the Department of Building

More information

FIRE RISK ASSESSMENT

FIRE RISK ASSESSMENT REGULATORY REFORM (FIRE SAFETY) ORDER 2005 FIRE RISK ASSESSMENT This template has been provided to assist the Responsible Person with the preparation of a Fire Risk Assessment and is not intended for commercial

More information

BS5839 Part 1:2002 Overview

BS5839 Part 1:2002 Overview BS5839 Part 1:2002 Overview 1 Contents Introduction So why is the current standard being revised? The brief for the new standard Changes to structure of current Standard Enhanced certification of Fire

More information

ACCESS AUDIT OF WESTPORT HOUSE

ACCESS AUDIT OF WESTPORT HOUSE ACCESS AUDIT OF WESTPORT HOUSE Large sign on the highway to indicate the entrance to Purbeck District Council Large and wide entrance Entrance showing sign for opening times Entrance sign Main entrance

More information

How To Write A Fire Risk Assessment

How To Write A Fire Risk Assessment Fire Safety Risk Assessment This form is to aid you in carrying out a fire safety risk assessment of a property. The form is separated in to two parts: Part 1 initial assessment form and guidance notes

More information

RESIDENTS FIRE SAFETY INFORMATION PACK

RESIDENTS FIRE SAFETY INFORMATION PACK RESIDENTS FIRE SAFETY INFORMATION PACK MARIE CURIE SCEAUX GARDENS ESTATE LONDON SE5 THE CONTENTS OF YOUR PACK Section Page No. 1. 3. Introduction Here we will explain the purpose of the Fire Safety Information

More information

Compliance Schedules and Building Warrant of Fitness

Compliance Schedules and Building Warrant of Fitness Compliance Schedules and Building Warrant of Fitness Purpose of this guidance information The purpose of this guidance information is to help building owners and managers of commercial, industrial or communal

More information

Fire Safety Requirements for Child Care Centre

Fire Safety Requirements for Child Care Centre Fire Safety Requirements for Child Care Centre A. Restrictions on Location Child care centre shall not be located : - (a) (b) in any premises designed for residential use; in any industrial building, warehouses,

More information

City of Bettendorf Fire Alarm System Requirements

City of Bettendorf Fire Alarm System Requirements City of Bettendorf Fire Alarm System Requirements Section 907 of the 2009 Edition of the International Fire Code (IFC) and Section 10-7-3 of the Municipal Code provide fire alarm requirements. IFC Section

More information

I.S. 3218 :2013 Fire Detection & Alarm Systems

I.S. 3218 :2013 Fire Detection & Alarm Systems I.S. 3218 :2013 Fire Detection & Alarm Systems Overview of significant changes 26 th March 2014 FPS Ltd Today s Programme Commencement Transition Competence & Qualifications System Certification System

More information

AVAILABLE TO DOWNLOAD ON THE APOLLO APP. Pocket guide to. Fire Alarm Systems Design BS 5839-1. Standard

AVAILABLE TO DOWNLOAD ON THE APOLLO APP. Pocket guide to. Fire Alarm Systems Design BS 5839-1. Standard Pocket guide to Fire Alarm Systems Design BS 5839-1 Standard AVAILABLE TO DOWNLOAD ON THE APOLLO APP The Regulatory Reform (Fire Safety) Order (FSO) became law on 1 October 2006 Legally you must comply!

More information

THE UNIVERSITY OF EDINBURGH. Paterson s Land.

THE UNIVERSITY OF EDINBURGH. Paterson s Land. THE UNIVERSITY OF EDINBURGH. Paterson s Land. BOOKABLE ROOMS ACCESS GUIDE. Address: Paterson s Land, Holyrood Road, Edinburgh, E,H,8, 8,A,Q. Telephone number: 0131 651 6138. Campus maps link: http://www.ed.ac.uk/maps?building=patersons-land

More information

BUILDING CONTROL GUIDANCE SHEET REPLACEMENT WINDOWS AND DOORS Last updated 16/11/2010

BUILDING CONTROL GUIDANCE SHEET REPLACEMENT WINDOWS AND DOORS Last updated 16/11/2010 Building Control Charnwood Borough Council Southfield Road Loughborough LE11 2TN BUILDING CONTROL GUIDANCE SHEET REPLACEMENT WINDOWS AND DOORS Last updated 16/11/2010 Page 1 of 6 PURPOSE: This Guidance

More information

Fire precautions in dwellings. Private sector housing Providing homes building communities

Fire precautions in dwellings. Private sector housing Providing homes building communities Fire precautions in dwellings Private sector housing Providing homes building communities Version 3 Published by Norwich City Council August 2011 Contents Page Introduction 1 2 Types of dwellings (A) Shared

More information

Learn how all this can be achieved. architecture AND save money. exceptional. with the SALT LAKE CITY, UT PERMIT # US POSTAGE PAID FIRST CLASS

Learn how all this can be achieved. architecture AND save money. exceptional. with the SALT LAKE CITY, UT PERMIT # US POSTAGE PAID FIRST CLASS The ONLY horizontal sliding fire-door with these unique features: Spans unlimited widths, heights up to 23 feet Meets fire codes without being seen Approved for egress applications Automatic closing and

More information

For use by landlords of small premises Premises Address

For use by landlords of small premises Premises Address fire risk assessment For use by landlords of small premises Premises Address FIRE RISK ASSESSMENT for use by landlords of small premises Person having control of the premises: Name of landlord (if different):

More information

City of Riverside Building & Safety Division Phone: (951) 826-5697 www.riversideca.gov

City of Riverside Building & Safety Division Phone: (951) 826-5697 www.riversideca.gov City of Riverside Building & Safety Division Phone: (951) 826-5697 www.riversideca.gov BUILDING CODE REQUIREMENTS FOR CHILD DAY CARE The purpose of this document is to provide the user with a basic level

More information

General Safety & Health Standards Published by the Division of Building Safety In Cooperation with the Idaho Industrial Commission

General Safety & Health Standards Published by the Division of Building Safety In Cooperation with the Idaho Industrial Commission General Safety & Health Standards Published by the Division of Building Safety In Cooperation with the Idaho Industrial Commission Local Fire Alarm 064. FIRE ALARM SYSTEMS 01. Scope 02. Definitions 03.

More information

The Regulatory Reform Fire Safety Order (RRFSO) and Healthcare guidance document Llandrindod Wells 10 May 2006

The Regulatory Reform Fire Safety Order (RRFSO) and Healthcare guidance document Llandrindod Wells 10 May 2006 The Regulatory Reform Fire Safety Order (RRFSO) and Healthcare guidance document Llandrindod Wells 10 May 2006 Prof David Charters, PhD, CEng, FIFireE Director of Fire Engineering Presented by Nigel Smithies

More information

FIRE-RESISTANT GLAZING Mr Leslie O May Sales Consultant Wright Style Limited England

FIRE-RESISTANT GLAZING Mr Leslie O May Sales Consultant Wright Style Limited England FIRE-RESISTANT GLAZING Mr Leslie O May Sales Consultant Wright Style Limited England Fire is a life-threatening and destructive force, which if unchecked, can spread rapidly through a building. Every year,

More information

RESIDENTS FIRE SAFETY INFORMATION PACK

RESIDENTS FIRE SAFETY INFORMATION PACK RESIDENTS FIRE SAFETY INFORMATION PACK PERRONET HOUSE PRINCESS STREET LONDON SE1 THE CONTENTS OF YOUR PACK Section Page No. 1. 3. Introduction Here we will explain the purpose of the Fire Safety Information

More information

How To Build A Basement House

How To Build A Basement House Single Family Basement Finish Purpose of Guide The purpose of this guide is to assist you in the permit process for your project. This handout is intended as a basic plan submittal under the 2009 International

More information

The Impact of the new Directive 2014/33/EU and Standard EN81-20 on New Lifts

The Impact of the new Directive 2014/33/EU and Standard EN81-20 on New Lifts The Impact of the new Directive 2014/33/EU and Standard EN81-20 on New Lifts Malta Lift Association Workshop Ing Ray Spiteri DMS, MBA (Brunel), B.Sc.. Mech Eng (Hons), EUR Ing, MIMechE, MASHRAE, MIAEE,

More information

FURNITURE & FURNISHINGS - FIRE SAFETY STANDARDS

FURNITURE & FURNISHINGS - FIRE SAFETY STANDARDS Fire Safety Technical Guide FURNITURE & FURNISHINGS - FIRE SAFETY STANDARDS 1.0. Introduction 1.1. Furniture and furnishings may significantly increase fire spread in rooms and those circulation spaces,

More information

HOUSING STANDARDS POLICY TRANSITION STATEMENT IMPLEMENTATION: OCTOBER 2015. May 2015

HOUSING STANDARDS POLICY TRANSITION STATEMENT IMPLEMENTATION: OCTOBER 2015. May 2015 HOUSING STANDARDS POLICY TRANSITION STATEMENT IMPLEMENTATION: OCTOBER 2015 May 2015 MAYOR OF LONDON Housing Standards: Transition Policy Statement. On 25 March 2015 through a written ministerial statement,

More information

For use by landlords of small premises Premises Address

For use by landlords of small premises Premises Address fire risk assessment For use by landlords of small premises Premises Address FIRE RISK ASSESSMENT for use by landlords of small premises Person having control of the premises: Name of landlord (if different):

More information

RESIDENTS FIRE SAFETY INFORMATION PACK

RESIDENTS FIRE SAFETY INFORMATION PACK RESIDENTS FIRE SAFETY INFORMATION PACK CASTLEMEAD CAMBERWELL ROAD LONDON SE5 THE CONTENTS OF YOUR PACK Section Page No. 1. 3. Introduction Here we will explain the purpose of the Fire Safety Information

More information

FIRE RISK ASSESSMENT COMPETENCY COUNCIL

FIRE RISK ASSESSMENT COMPETENCY COUNCIL FIRE RISK ASSESSMENT COMPETENCY COUNCIL Competency Criteria for Fire Risk Assessors Version 1 Published : 21/12/11 Page 1 Foreword Fire safety legislation requires that, for most premises except private

More information

SECTION 903 AUTOMATIC SPRINKLER SYSTEMS

SECTION 903 AUTOMATIC SPRINKLER SYSTEMS Page 25 ABOUT CODE CORNER CCFS would like to remind you to check with your local Authority Having Jurisdiction (AHJ) for questions and opinions concerning your local Fire and Building Codes. The information

More information

BS9999 and FRAME. FRAME and BS 9999

BS9999 and FRAME. FRAME and BS 9999 BS9999 and FRAME. BS9999 and FRAME....1 The approach of BS9999 compared with FRAME...3 Introduction...3 General Information in Section 1....3 Assessing risk (clause 5) and Risk Profiles (clause 6)....4

More information

EVACUATION & LIFE SAFETY STRATEGIES FOR SUPER HIGH RISE BUILDINGS. Sam Aloi, Grad. Dip. (Fire Safety & Risk Eng.)VUT Melb, BE (Building) VUT Melb.

EVACUATION & LIFE SAFETY STRATEGIES FOR SUPER HIGH RISE BUILDINGS. Sam Aloi, Grad. Dip. (Fire Safety & Risk Eng.)VUT Melb, BE (Building) VUT Melb. EVACUATION & LIFE SAFETY STRATEGIES FOR SUPER HIGH RISE BUILDINGS By Sam Aloi, Grad. Dip. (Fire Safety & Risk Eng.)VUT Melb, BE (Building) VUT Melb. & Jason Rogers, Grad. Dip. (Fire Safety & Risk Eng.)VUT

More information

Vestibule Case Study. Vestibule Requirement Intent [2003 IECC, 2006 IECC, 2003 IBC, 2006 IBC, 90.1-2001, 90.1-2004]

Vestibule Case Study. Vestibule Requirement Intent [2003 IECC, 2006 IECC, 2003 IBC, 2006 IBC, 90.1-2001, 90.1-2004] Vestibule Case Study [2003 IECC, 2006 IECC, 2003 IBC, 2006 IBC, 90.1-2001, 90.1-2004] Vestibule Requirement Intent Page 1 of 14 The primary intent behind the requirement for a vestibule is to reduce infiltration

More information

Construction Warehouse. Culminating Experience in Fire Protection Engineering FPE 596 Prepared by Ben Johnson

Construction Warehouse. Culminating Experience in Fire Protection Engineering FPE 596 Prepared by Ben Johnson Construction Warehouse Culminating Experience in Fire Protection Engineering FPE 596 Prepared by Ben Johnson Construction Warehouse Waste Treatment and Immobilization Plant (WTP) Project U.S. Department

More information

Workplace Health, Safety & Welfare

Workplace Health, Safety & Welfare Relevant Legislation Workplace (Health, Safety and Welfare) Regulations 1992 Construction (Design & Management) Regulations 2015 Provision & Use of Work Equipment Regulations 1998 (PUWER) Lifting Operations

More information